amstone110 Posted May 7, 2013 Posted May 7, 2013 I am trying to install 4 residential LOR controllers this year. I want to install each controller onto two 15amp breakers so that each side is getting the recommended 15 amps. The problem is that if I am installing 4 controllers, that means I need room to add 8 15 amp breakers, which I don't have the room for in my panel. Also, the main line on the outside of my house from the power company is rated at 200 amps, and it has 4 breakers on it outside, then is ran to the subpanel on the inside of my house which has the remainder of the breakers. I'm not certain how many amps are being ran to the sub panel (looks like 1/0 awg power cable), but will this panel even be able to handle 120 amps of breakers even if I did have the room? I am considering adding 4 30 amp breakers, and having them run to RV outlets, then buying an adapter cord which splits it into two 15 amp outlets. This will allow me to only have to install 4 more breakers in my box. The adapter cable (www.amazon.com/gp/aw/d/b007577nlu/ref+mp_s_a_1?qid=1367939428&sr=8-8π=sl75 ) cost 22 dollars and the RV plug is around 8. A 30 amp breaker is around 10 so the total per LOR controller would be 40 dollars. With 4 controllers I'm looking at around 160+ dollars. Is there a cheaper and better way of doing it? Can I install a second sub-panel just for them? How do people with 10+ controllers power them? Do you have to upgrade your main supply power coming from the street? Any help would be greatly appreciated.
Ron Boyd Posted May 7, 2013 Posted May 7, 2013 I ran 7 controllers last year on 1, 20 amp circuit, and, a 5 ft^3 freezer with no problems whatsoever. I built a box with 8 receptacles and 2 pigtails. Plugged the 2 pigtails into the outside circuit, and then ran the extension cords for the controllers from there. If you're using LEDs, you will have zero problems with 1 circuit. No need for upgrading. Get you one of these: http://www.amazon.com/P3-International-P4400-Electricity-Monitor/dp/B00009MDBU Hook up a controlles with all channels on at 100% and see how many amps you're pulling. Mine last year was roughly 0.7 amps per controller. I had 1 string of 70 ct LEDs on each channel 1
Don Posted May 7, 2013 Posted May 7, 2013 I agree with Ron. It all depends on what you are going to be using in your display. If your display adds up to a total of 35 amps then you only need a total of 3, 15 amp circuits to run the display. How you have them connected to the home outlets would be dependent on how you have the load distributed across the controller, etc.
amstone110 Posted May 7, 2013 Author Posted May 7, 2013 I meant to mention this, I have all incad's (about 12,000) and about 25 strands (25ct) of C9's that I am running. My spotlights I am running off separate outlets and using relays with the LOR controller only doing on/off.
amstone110 Posted May 7, 2013 Author Posted May 7, 2013 I ran 7 controllers last year on 1, 20 amp circuit, and, a 5 ft^3 freezer with no problems whatsoever. I built a box with 8 receptacles and 2 pigtails. Plugged the 2 pigtails into the outside circuit, and then ran the extension cords for the controllers from there. If you're using LEDs, you will have zero problems with 1 circuit. No need for upgrading.Get you one of these: http://www.amazon.com/P3-International-P4400-Electricity-Monitor/dp/B00009MDBUHook up a controlles with all channels on at 100% and see how many amps you're pulling. Mine last year was roughly 0.7 amps per controller. I had 1 string of 70 ct LEDs on each channelIt's funny that you mentioned this item. I forwarded it to my wife just yesterday suggesting she should buy me one.
Don Posted May 7, 2013 Posted May 7, 2013 I meant to mention this, I have all incad's (about 12,000) and about 25 strands (25ct) of C9's that I am running. My spotlights I am running off separate outlets and using relays with the LOR controller only doing on/off. Last I looked a 25ct strand of incandescent C9's were running about 1.46 amps each. That right there would be 36.5 amps.
MCas4380 Posted May 8, 2013 Posted May 8, 2013 you can always steal power from other places like the garage. Or the Neighbors
Max-Paul Posted May 8, 2013 Posted May 8, 2013 Good grief, I would think that between the upgrade to your power panels and the power cost to run them. That upgrading to LED might be cost effective. I ran about 8 AC and 1 DC controller a couple years back. With a Kill A Watt inline and all on at 100%. My current draw was at 10 amps. I have added 36 strings of 100 ct C6 for my mega tree and 5 trees with about 450 ct each. I have not checked to see how much current draw was added. But I didnt trip the 15 amp breaker all last year.
kiplorenzo Posted May 8, 2013 Posted May 8, 2013 I actually had an licensed and insured electrician out this last week to get a quote on a 60 amp circuit in the front yard... He also said that my panel would need to be replaced as it was using aluminum...Total cost to replace the panel and and the circuit was 6500.00. I think I'll get more bids as I will also be powering a water feature. Kip
amstone110 Posted May 8, 2013 Author Posted May 8, 2013 I actually had an licensed and insured electrician out this last week to get a quote on a 60 amp circuit in the front yard... He also said that my panel would need to be replaced as it was using aluminum...Total cost to replace the panel and and the circuit was 6500.00. I think I'll get more bids as I will also be powering a water feature.Kip 6,500? Or 650? There's no way it should cost 6500.
MCas4380 Posted May 8, 2013 Posted May 8, 2013 6,500? Or 650? There's no way it should cost 6500.I agree 6,500 seems like way to much.
Dennis Laff Posted May 8, 2013 Posted May 8, 2013 Added 60amp subpanel 50 feet away from main two years ago by lic electrian cost $350.00
kiplorenzo Posted May 8, 2013 Posted May 8, 2013 It was 6500.00 total.... which is why I am taking more bids... I originally wanted Licensed and insured as if anything happens to the house, then I come back on them. but I have a friend that had a licensed electrician do all the work for around 500.00 he had to have electricity run to his barn.
Max-Paul Posted May 9, 2013 Posted May 9, 2013 Also they make a NO-OX compound to keep the Al from oxidizing and fire issues. So, I am not sure why he would have to replace the panel cause of the Al. Ya, someone made a mistake on the 6K figure.
steve synek Posted May 9, 2013 Posted May 9, 2013 I am trying to install 4 residential LOR controllers this year. I want to install each controller onto two 15amp breakers so that each side is getting the recommended 15 amps. The problem is that if I am installing 4 controllers, that means I need room to add 8 15 amp breakers, which I don't have the room for in my panel. Also, the main line on the outside of my house from the power company is rated at 200 amps, and it has 4 breakers on it outside, then is ran to the subpanel on the inside of my house which has the remainder of the breakers. I'm not certain how many amps are being ran to the sub panel (looks like 1/0 awg power cable), but will this panel even be able to handle 120 amps of breakers even if I did have the room? I am considering adding 4 30 amp breakers, and having them run to RV outlets, then buying an adapter cord which splits it into two 15 amp outlets. This will allow me to only have to install 4 more breakers in my box. The adapter cable (www.amazon.com/gp/aw/d/b007577nlu/ref+mp_s_a_1?qid=1367939428&sr=8-8π=sl75 ) cost 22 dollars and the RV plug is around 8. A 30 amp breaker is around 10 so the total per LOR controller would be 40 dollars. With 4 controllers I'm looking at around 160+ dollars. Is there a cheaper and better way of doing it? Can I install a second sub-panel just for them? How do people with 10+ controllers power them? Do you have to upgrade your main supply power coming from the street? Any help would be greatly appreciated. Amstone I have to admit I am not familiar with that splitter you are showing in the link......but have to ask where is the GFCI protection? My two cents is that that method is not acceptable. You need to plug your controllers into 15 or 20 amp GFCI protected outlets. Seek some help from an electrician. Steve Steve 1
Steven Posted May 9, 2013 Posted May 9, 2013 but have to ask where is the GFCI protection? My two cents is that that method is not acceptable. You need to plug your controllers into 15 or 20 amp GFCI protected outlets. I agree with this.Ungrounded, outdoor lighting, at >50v, which is what most of us do here, requires GFCI. (You can build a safe system without GFCI by enclosing everything in a metal grounded case, or only using low voltage, but this is usually not feasible.) 30A wall outlets (regular or GFCI) are not made. The ones you find in your house are typically 15A, and the ones with the 'T' shaped neutral are 20A. It is not allowed to connect a 20A outlet to a 30A circuit. (Although it is allowed to install multiple 15A outlets on a 20A circuit.)Therefore, your setup must use 20A or 15A circuits (and breakers). Either the sockets or the breakers must be GFCI. You can't connect NEMA 5 outlets to a 30A circuit. 2
lowepg Posted September 25, 2013 Posted September 25, 2013 but have to ask where is the GFCI protection? My two cents is that that method is not acceptable. You need to plug your controllers into 15 or 20 amp GFCI protected outlets. I agree with this. Ungrounded, outdoor lighting, at >50v, which is what most of us do here, requires GFCI. (You can build a safe system without GFCI by enclosing everything in a metal grounded case, or only using low voltage, but this is usually not feasible.) 30A wall outlets (regular or GFCI) are not made. The ones you find in your house are typically 15A, and the ones with the 'T' shaped neutral are 20A. It is not allowed to connect a 20A outlet to a 30A circuit. (Although it is allowed to install multiple 15A outlets on a 20A circuit.) Therefore, your setup must use 20A or 15A circuits (and breakers). Either the sockets or the breakers must be GFCI. You can't connect NEMA 5 outlets to a 30A circuit. I'm also expanding from 1 to 4 controllers this year... Are you saying each controller needs a 15-20a circuit? Wouldn't that depend on the load / controller? I do NOT have a dedicated circuit for each box....
steve synek Posted September 25, 2013 Posted September 25, 2013 (edited) I'm also expanding from 1 to 4 controllers this year... Are you saying each controller needs a 15-20a circuit? Wouldn't that depend on the load / controller? I do NOT have a dedicated circuit for each box....Yes it would depend on the load..........there are lots of LED user who run thousands of lights on a single circuit.......and use lots of controllers................ Edited September 25, 2013 by steve synek
Steven Posted September 25, 2013 Posted September 25, 2013 Are you saying each controller needs a 15-20a circuit? No, what I am saying is that you can't use a 30A circuit.
DaGoose Posted September 28, 2013 Posted September 28, 2013 I am not an electrician but I know a little something about it. If he said $6500 it may be correct, especially if it is aluminum wiring, in the 60's and 70's electricians wired houses with aluminum wiring. Aluminum requires a larger gague to carry the same load as copper. If you run a standard 12-3 copper wire for a 20 amp circuit, they don't even make an equvilent size that small in aluminum wire, the smallest gague in aluminum is 6 gauge and it is very dangerous to wire copper (today's wire) and the aluminum wiring so he may be taking about rewiring the house to a safer copper standard box and wire. 1