 I have a 16pcg3 controller, but am having problems showing I have 16. according to the hardware utility i have only 8. how do I change this

Posted

Are you saying that you ran the hardware utility detection with just the one controller attached, and it detected the device as a 16pcg3 and only showed 8 channels you could turn on?

Posted

You have me a bit confused. 8 what?

the 16PC G3 should only appear as 1 ID. You need that to be one of   01,02,03,04  (01 is  what they ship as, and what most folk us for their first controller)

The controller ALSO has 2 power cords. Both need to be plugged into Power to use 16 outputs , (1 of these cords, also provides Logic Power , the Green LED will show that power is applied by coming on: flashing=power only, Steady LOR Net connected)