Channels 1-8 fail to work. I checked power to it, replaced fuse, checked that the lights to be connected works, The I D # which is set at 0- 2 it is #2 controller. I have the LOR1602. Thanks for any replies.

Link to comment
Share on other sites

Does your unit have 2 input power cords or 1?

If has 2 are both plugged in?

If only has one do you have the hot and neutral jumpers installed on the board where it is noted?

The electronics on the board are powered from the right side of the board. Meaning channels 9-16.

Chuck

Link to comment
Share on other sites

Hi chuck, it has two plugs and no I did not check the jumper, the box is in second time use and I stored it over the year, maybe the jumper came off. Right now its still dark here in Reno and the control boxs is mounted on my second floor, I plan to go up as soon as I get a little sun light. Thanks

Link to comment
Share on other sites

cmoore60 wrote:

don't need the jumper if you have to power cords.

Not only do you not need it, you don't want it. It would (could) be bridging two separate circuits on your panel otherwise.
Link to comment
Share on other sites

cmoore60 wrote:

Thank you for adding the clarification.


I never like taking chances with electrical stuff! ;)