Eric walls Posted December 9, 2014 Share Posted December 9, 2014 I searched this forum and found a little information but I still have a question regarding a GFCI receptacle I have. 2 controllers are plugged into it running my 16 channel mega tree and my arches. My arches are made out of pvc and the the pugs go through the middle of the pvc pipe and then to the controller. All plugs are off the ground. On my mega tree my stands come down from the top of the tree to a tent stake and then back up a few feet. Again all the plugs are off the ground on this one.The totally amps for both controllers and the lights and less than 1, so I don't think the plug is being overloaded. During the show it will run for a few minutes and then pop. I reset the plug but then it pops again after a few seconds. Oe of the suggestions in another thread suggested the plug doesn't like the fast action of the controllers and sees this as a problem, and pops the receptacle. A friend of mine said he tries to find non GFCI plugs for his equipment for that very reason. Should I replace the plug? It's an outside plug and code requires it to be a GFCI plug but I was considering changing it to a regular plug. Would this be dangerous? I really can't find why it would pop, and it's frustrating to see only part of my show. Link to comment Share on other sites More sharing options...
Liberty-Laser Posted December 9, 2014 Share Posted December 9, 2014 (edited) GFCIs do go bad. Replace it with a new one. A regular outlet is cheaper, but offers no protection. Be sure you replace with a quality GFCI outlet. I should add that after a similar experience I discovered 2 GFCI outlets on the same circuit. Once I removed one, the circuit and GFCI worked normally. Edited December 9, 2014 by Liberty-Laser Link to comment Share on other sites More sharing options...
ItsMeBobO Posted December 9, 2014 Share Posted December 9, 2014 I had one go bad as well. Would trip very easily. New one working much better. Link to comment Share on other sites More sharing options...
Liberty-Laser Posted December 9, 2014 Share Posted December 9, 2014 A couple years ago, I replaced most of my display GCFIs with a model that had a green lamp when working properly. Great for quickly identifying a popped outlet, or just peace of mind that at a quick glance, you know all GFCIs are up and running. Link to comment Share on other sites More sharing options...
vkjohnson Posted December 9, 2014 Share Posted December 9, 2014 I agree above, replace the GFCI with a new GFCI outlet. Link to comment Share on other sites More sharing options...
Eric walls Posted December 9, 2014 Author Share Posted December 9, 2014 Thanks guys. I think today after work I'll go down to our hardware store and get a very good one. Shouldn't take too long to replace. I'm tempted to replace it with a regular plug but I don't think that would really be safe or within code. During the rest of the year I use that plug for my string trimmer and other landscape appliances. Link to comment Share on other sites More sharing options...
Jim Hans Posted December 9, 2014 Share Posted December 9, 2014 Replace it with another GFCI! If the GFCI is bad, the new one you install won't trip. If the new one trips it is telling you that you have an electrical problem. Ignoring that by putting in a regular plug could cause someone to get zapped! Link to comment Share on other sites More sharing options...
Eric walls Posted December 9, 2014 Author Share Posted December 9, 2014 Ya, exactly what I was thinking. Someone suggested putting a regular outlet on there but I don't think that's a good idea. I'd rather have it trip a bunch of times than to get zapped, just not worth it. If it still trips all the time then I'll just have to figure out another place to plug the controllers in to, and/or troubleshoot the electrical problem. My house was built just 15 years ago and some of the outside plugs are GFCI and some are not. Wonder why they did it that way? Link to comment Share on other sites More sharing options...
SparkDr Posted December 9, 2014 Share Posted December 9, 2014 I'd try plugging a corded power tool into the GFI and try to run that through a bunch of on & off cycles before replacing the receptacle. Something like a circular saw with a high inrush current that puts a lot of noise on the line. If the GFI holds, your problem is probably elsewhere. 1 Link to comment Share on other sites More sharing options...
SparkDr Posted December 9, 2014 Share Posted December 9, 2014 Ya, exactly what I was thinking. Someone suggested putting a regular outlet on there but I don't think that's a good idea. I'd rather have it trip a bunch of times than to get zapped, just not worth it. If it still trips all the time then I'll just have to figure out another place to plug the controllers in to, and/or troubleshoot the electrical problem. My house was built just 15 years ago and some of the outside plugs are GFCI and some are not. Wonder why they did it that way?Those outside non-GFCI receps are probably fed in a line-load configuration from another GFCI upstream in the circuit. It's pretty common to see outdoor receps fed off a bath GFCI in a lot of new construction residential projects. It seems like an awful nuisance to me to have to go inside to reset a tripped GFI just to save a few bucks on the job, but that's just my 2 cents. Link to comment Share on other sites More sharing options...
KStatefan Posted December 9, 2014 Share Posted December 9, 2014 Those outside non-GFCI receps are probably fed in a line-load configuration from another GFCI upstream in the circuit. It's pretty common to see outdoor receps fed off a bath GFCI in a lot of new construction residential projects. It seems like an awful nuisance to me to have to go inside to reset a tripped GFI just to save a few bucks on the job, but that's just my 2 cents. My parents house is the opposite and the bathroom is fed form the outside GFCI. Link to comment Share on other sites More sharing options...
Eric walls Posted December 9, 2014 Author Share Posted December 9, 2014 So would it be possible then that the non GFCI plug could be causing the GFCI plug to trip? The non GFCI plug goes to my mini trees which are wire frame. Would it help to zip ties the cord off the ground or do I still need something under the wire frame? Why do they wire houses like that? Link to comment Share on other sites More sharing options...
Liberty-Laser Posted December 9, 2014 Share Posted December 9, 2014 (edited) So would it be possible then that the non GFCI plug could be causing the GFCI plug to trip? The non GFCI plug goes to my mini trees which are wire frame. Would it help to zip ties the cord off the ground or do I still need something under the wire frame? Why do they wire houses like that? If you are using wire-frames & incandescent, they are a pain. After switching to LED, I have had no issues with mine. I did limit the issue while using incandescents by coating the metal prongs (that go into the ground) with either a rubber dip or spraying with that stuff they sell to seal gutters. May be the same stuff in a different form. The other part of your question, Yes, if the non GFCI outlet is in parallel - further down the wire from a GFCI outlet. The one GFCI protects both. Edited December 9, 2014 by Liberty-Laser Link to comment Share on other sites More sharing options...
SparkDr Posted December 9, 2014 Share Posted December 9, 2014 If you can confirm that the non-GFI receptacle is downline in the same circuit fed through the GFI, then yes, it is entirely possible that something plugged into a non-GFI recep would cause an upline GFI to trip. As for why this sort of wiring is done, it's beyond me. I've done residential electrical work for 15+ years and I wire all my GFI's as stand-alone for convenience and ease of troubleshooting. I wind up using a lot more $10 GFI receps instead of 50 cent regular recepts, but it's my own preference. The #1 place I use downline receps fed from an indoor GFI is in my display circuits. I have a row of GFI receps wired in right next to my panel feeding regular receps outside. If I have to change out or reset a GFI, I'm doing it in the comfort of my warm, well-lighted basement instead of kneeling down in the snow and cold outside. Link to comment Share on other sites More sharing options...
Eric walls Posted December 9, 2014 Author Share Posted December 9, 2014 Sorry if this topic has been brought up before…..I looked earlier and couldn't figure out and answer but I know it's probably been talked about a few times here.So it sounds like I could possibly have 2 issues. #1 could be the bad plug in which cade I'm join got replace it away with a better one. #2 could be the non GFCI elements causing the GFCI to trip if it's down from that circuit. In either case I will work on both and see if that helps. Seems like when they construct a subdivision the builders go the cheapest way they can. Even my main breaker box in the garage is very tiny, no from to add any circuits. I'd like to add a few dedicated circuits to run my lights and put the plugs in a more convent place, so I don't have to run extension cords across the lawn. Guess I'll either have to have a bigger box put in or a sub panel.Funny thing is when I lived in another older home it had a basement with a very large breaker box. I added a circuit for a freezer to hold fish/bait, and several other circuits for a window air conditioner. It was easy to crawl under the house and come up through the wall.These newer homes are much harder to do that and I don't know enough about electrical work to do that. I just want my lights to work! Link to comment Share on other sites More sharing options...
Mega Arch Posted December 9, 2014 Share Posted December 9, 2014 (edited) You can now purchase weather resistant outdoor grade GFCI receptacles, like Leviton WT899-W. They are only a few bucks more than the previous styles. I've had zero nuisance trips in 2 years after installing them. This model is also tamper resistant, so you don't get bugs in the hot or neutrals during the off-season. Ran the show last week in fog, mist & rain. No trips. Use quality receptacles and keep your plugs off the ground and the show will go on. Edited December 9, 2014 by Mega Arch Link to comment Share on other sites More sharing options...
Eric walls Posted December 9, 2014 Author Share Posted December 9, 2014 Going to pick one up today right after work. Thanks everyone! Link to comment Share on other sites More sharing options...
SparkDr Posted December 9, 2014 Share Posted December 9, 2014 Just an FYI - the only features that differentiate weather resistant GFI receptacles are a UV stabilized, high cold impact resistant thermoplastic face and a stainless steel mounting face. internally, they are the same and are required to trip at the same 5 mA threshold as any other GFCI. Are they better? Maybe, but definitely not in the way most of us would think. A 5 mA fault isn't going to care about better plastic and a non-corrosive strap. Mega Arch's success is likely more attributable to the tamper-resistant closure feature and overall quality that Leviton brings to their products (yes, I'm a big fan of them vs other brands). Add in the fact that they are new and have not been through any trip cycles and/or suffered from any internal corrosion on the contacts as yet and it's a whole bunch of positives in your favor to help keep the lights on. Link to comment Share on other sites More sharing options...
Mega Arch Posted December 10, 2014 Share Posted December 10, 2014 Been selling electrical supplies for 33+ years. Just saying for $1.75 more, they're the best I've ever sold. Link to comment Share on other sites More sharing options...
Max-Paul Posted December 10, 2014 Share Posted December 10, 2014 (edited) Eric, if you dont want to be the laughing stock at the hardware store. Call it what it is. It is a SOCKET. A PLUG is what you have in your hand and put it in the socket. Calling a socket a plug is like calling yourself a female. Are you a plug or a socket Eric? Edited December 10, 2014 by Max-Paul Link to comment Share on other sites More sharing options...