I have 4 CCRs and I have been testing running them and at first I thought I had a bad CCR controller. After various tests I've figured out that somehow commands from one CCR bleed over to the other. If I have commands sent to one controller then it does exactly what I expect. If I have commands sent to the next controller then the 1st controller seems to use the commands for controller 1 plus some of the commands of controller 2. I am going to try and connect the 2nd controller and see if the commands pass all the way though instead of bleeding/getting stuck on the first controller. Anyone seen anything like this????

Edited by LORAdmin
Link to comment
Share on other sites

Make sure the controller configurations do not specify legacy unit id mode, but rather normal unit id mode.

Link to comment
Share on other sites

Use LOR Legacy mode (maximum circuit - 16) is NOT checked. Is that what you meant?

Automatically link channel settings IS checked

Link to comment
Share on other sites

Use LOR Legacy mode (maximum circuit - 16) is NOT checked. Is that what you meant?

Automatically link channel settings IS checked

No, use the Hardware Utility. Refresh to find your CCRs then look at their configurations. Make sure they are all in normal unit ID mode.

Link to comment
Share on other sites

  • 4 weeks later...

They were to be changed last year. I had the same issue back in March. Dan said he would have them shipped in normal mode.