crackchecker Posted November 2, 2010 Share Posted November 2, 2010 I have one channel currently not working on a recently finished board. But that's not the question at hand.While in the Hardware utility, LOR Control, Test Unit's operation, "mode" Test inputs (for interactive). The controller inputs are showing inputs 1, 2, and 3 show as having switches connected and marked GREEN for being triggered.Is this a sign of bigger problems or is this common? When testing lights, all the channels work (steady, shimmer, twinkle, and fade) except the #6. Link to comment Share on other sites More sharing options...
Max-Paul Posted November 2, 2010 Share Posted November 2, 2010 I believe that all of the inputs float high or on. It is when you add a N.O. momentary switch and close the switch the input is grounded and shows as off. So, you could say that the inputs are pulled high with no load applied. Link to comment Share on other sites More sharing options...
cmoore60 Posted November 2, 2010 Share Posted November 2, 2010 The trigger inputs can be configured either N.O. or N.C. on the configure tab in the hardware utility. The color is just an indicator of the status of the input in reference to the way it is configured.Chuck Link to comment Share on other sites More sharing options...
LightORamaDan Posted November 3, 2010 Share Posted November 3, 2010 Without the input header in place, the input 2 and 3 will float as mentioned by Paul-Max... Also as cmoore60 mentioned the input can be configured as N.O. or N.C. ...I would expect the results to be random when just checking as you did.Dan Link to comment Share on other sites More sharing options...