The line from the main box is #6 Romex and only about 50 feet long. Each outlet has been "snipped" to allow for two circuits on one outlet. The wire from the breakers to the outlets is #12.

I just finished making 22 mini tree's from 2 tomato cages each. Uuuugghh.. I think that I shall have nightmares of Tomato cages and Zip ties chasing me for several weeks to come. lol..

Thanks in advance.


Attached files 73636=4541-DSC02436.jpg

Link to comment
Share on other sites

I don't think that twisting the grounds together is up to code. Here is what you should use instead. You can get them at home depot or lowes or any electrical supply shop.



Edit: I just noticed your wire sizes. I would check to make sure your wire size is adequate. This link should help. http://www.planetchristmas.com/WireSize.htm

I don't want to bash your work but I wouldn't want you to have a fire.


Attached files 73646=4548-pACE2-976322dt.jpg

Link to comment
Share on other sites

The main box looks good from what I can tell (can't tell wire sizes, etc). 20A breakers need #12 wire (or larger), 15A need #14 (or larger).

That "rubbermaid container" definitely wouldn't pass an inspection, though. Technically you should run the conduit down to your outlet boxes (you'd have to use a different style). What is the purpose of the rubbermaid container? I doubt it's waterproof in that configuration, and it doesn't look like you're outside anyway...

EDIT: Ok I looked again, and maybe you are outside? In that case, you should replace the outlet boxes with proper outdoor rated ones, then use "in-use" covers on each of them. Then you can scrap the rubbermaid box, which I doubt is weatherproof in that configuration on its side anyway...

In use cover:

6198923.JPG
-Tim

Link to comment
Share on other sites

Don't plan on pulling a full load on #6 as it is very under rated for that load. What size is your breaker that feeds this panel? Tie your grounds in with your neutral bar and consider another ground rod. As mentioned, local code in my area specifies the nice little boxes with the clear covers that will close while plugged in.

Other than that, it looks like a good clean job. I do not see an issue with using Ceel-Tite, It has a better rating than your box (I assume the box is rated 3X?)

Link to comment
Share on other sites

Eric R wrote:

Tie your grounds in with your neutral bar

No don't do that. It's a code violation to tie grounds and neutrals together anywhere but your main service panel. In any subpanel, they must be kept separate. As mentioned above, you should use a separate grounding bus. Not sure code will like them all just twisted together, although I personally can't imagine that being an actual hazard as long as they have a good connection together.

-Tim
Link to comment
Share on other sites

tfischer wrote:

Eric R wrote:
Tie your grounds in with your neutral bar

No don't do that. It's a code violation to tie grounds and neutrals together anywhere but your main service panel. In any subpanel, they must be kept separate. As mentioned above, you should use a separate grounding bus. Not sure code will like them all just twisted together, although I personally can't imagine that being an actual hazard as long as they have a good connection together.

-Tim

My bad, you are correct Tim. I looked at the code.
Link to comment
Share on other sites

Did you apply for a permit from your local city hall? They are usually very helpful and can tell you exactly what is required, and will do an inspection to make sure everything is up to code. This is a must.

I'm not a licensed electrician but I've got a lot of experience and I see several problems. Is that a 100amp rated subpanel attached to a 2 pole 100amp breaker? If either is a no you've got a problem.

Second, according to my NEC chart, the feeder hot wires should be #2 copper- not #6! There needs to be a grounding wire that runs from your main panel to the subpanel and connects to a grounding bar. The conduit looks too small to handle the larger size wires.

Third, as mentioned, the rubbermaid container isn't Kosher. Each 12 Ga wire needs to be in conduit connecting to (10) individual waterproof outlet boxes (one for each circuit), with appropriate covers. I would install 20amp GFCI duplex outlets in each box.

Fourth, the grounding wires have been cut too short, and each needs to attach to grounding bar.

PLEASE talk with your local building inspector and/or a licensed electrician to get specifics on what is required for your area. It will save a lot of problems and worries in the future. :}

Link to comment
Share on other sites

So what does the code say about rubbermaid containers? document.write('tongue.gif');tongue.gif Other than that, I think you're good. I would replace those boxes with ones having conduit knockouts, and you'd be OK.

As far as the ground wires go, it isn't pretty, but I don't believe the code requires a grounding bar (although I'd use one). You do need to do two things if you don't use a ground bar. You need to put some sort of connector on that. You can't have them just twisted together. Either a big wirenut (if they make one that big), a crimp sleeve, or possibly a split bolt would work (although technically, split bolts aren't rated for that many wires). Second, you need to have the box bonded to ground. I don't see a ground wire going to the box itself? If you installed a ground bar, the box gets grounded automatically since the bar is bolted to the box.

Link to comment
Share on other sites

One more thing - those aren't the correct fittings for that sealtite. Those are PVC fittings. For the sealtite, you need a compression fitting specifically designed for that conduit. I wouldn't consider that a safety hazard, but it doesn't meet code either.

Link to comment
Share on other sites

Install a ground bar, if wire are to short, it ok to splice in the panel, this will also ground the panel.

Do not install the bonding screw that comes with all panel, this is used for when the panel is installed for your main service, you panel is a sub panel.

Install no larger then a 60 AMP 2-pole breaker feeding your sup panel, # 6 wire is only rated for 60 AMP.

Use weather proof box's and covers out side, with GFCI receptacle.

Use correct fittings with seal tight flex or PVC pipe.

Over all I think you did a great job.

Link to comment
Share on other sites

Yes, it's a 100A panel but as you see I am only using it for 40 amp. It will never get over 40 and that's what the #6 is rated for. Actually 50 so I am under there. As for the rubbermaid, somebody else had done this on their setup last year and suggested it and his pictures got a lot of raves. It's all temporary.

Everything else was talked about here and at Home Depot and was ok then. Snipping the outlets into separate circuits too.

Thanks

Link to comment
Share on other sites

As for the ground, they are wired in pretty tight.

You need to use the ground bar or a split bolt to tie all the ground together, even if they are wired tight, per NEC. The ground bar is the best, remember you dealing with electricity, if you do not give it the path it need to go to ground it will find it own path to ground, and it could be YOU.

Link to comment