Light-O-Rama Forums

how many 100mini lights strings of 0.33 Amps to a channel?


trinidad

Recommended Posts

Hello to all of you! Looking for help. if the controller is 30 amps - 15 per each side - how many 100mini lights strings of 0.33 can i connect to each channel? i want to use one 16 channel controller to animated a mega Christmas Tree. Please let me know.

thanks

Link to comment
Share on other sites

there are so many ways to tackle this question. if you want all lights on at the exact same time then you could add 5 strands per channel. that's a total of 80 strands of lights if you're going to have half the lights on and half of them off at the same time then you could add more strands. to keep it simple stick with 5 strands per channel and sequence it however you want you won't have to worry about anything. make sure each bank is plugged into its own 15 or 20 amp outlet

Edited by Sabre03
Link to comment
Share on other sites

Guest wbottomley

At the top of this forum, it says "This specific forum is to be used to ask questions related to the new forum software. Please do not use this forum for Light-O-Rama specific questions, as this specific forum is not expected to be here permanently."

You need to post these questions in the appropriate area.

Link to comment
Share on other sites

Math? Pfth, asked the right person.

This is simple...

Make it easier 30÷2 & 16÷2 = 15 Amps for 8 Channels

15÷8= 1.875 Amps per Channel

Now

1.875÷0.33 = 5.681

So ALWAYS round down with lights

1 Channel will support 550 Mini-Incandescent Lights, if you are using Heavy duty, they use more power.

Invest in a cheap Watt-O-Meter http://www.ebay.com/itm/P4400-P3-Electricity-Meter-Kill-a-watt-Usage-Monitor-/261094493618?pt=LH_DefaultDomain_0&hash=item3cca71cdb2

I have one, it works wonders and is very accurate. I never burn fuses anymore, because stray voltages, out lights and bad fuses can all affect amp draw.

Link to comment
Share on other sites

Math? Pfth, asked the right person.

This is simple...

[snip...]

Your math may be right, but your assumptions are all wrong ;)

Yes, the max per side is 15A, but the absolute max of any ONE channel is 8A.

It is perfectly acceptable to have 45 strings on at a single time: 24 strings on a single channel, and 21 on a second all at .33/a each or 8A on channel 1 and 7A on channel 2. (Of course, this all assumes you are using the high-power heat sinks).

So why can't I use 45 strings (15A) on a single channel?

Because the triacs (the solid-state devices that turn the lights on and off) are only rated to 8A.

Why can't I use 8A on a triac rated for 8A without a heatsink?

Because heat is what kills triacs, and they are ONLY rated to 8A when a proper heat sink is used.

  • Like 3
Link to comment
Share on other sites

... So, what's the max number of strings I can have on a light controller? Would you believe it if I said 'Nearly unlimited'? Well, not really unlimited, but a whole lot more than you expect:

In the above example I showed where you could have 24 strings on a single channel. And you can. All day long. But that's not really the MAX, that's the MAX at FULL BRIGHTNESS. Can you run 48 strings without burning up a triac or controller? Sure! just keep the intensity turned down.

Now wait a second! Don't think you can run 48 strings at 50%! What we are talking about is electricity and that means it's not a linear relationship. If I remember my theory correctly, dividing the duty cycle (of the AC wave) in half, does not mean a one-half reduction in amperage consumed.

... which is why when we talk about load per channel we always tend to talk in Maximums. That keeps your equipment safe.

Sorry folks. Remember when your 10'th grade math teacher told you you would someday need what he/she was teaching? Surprise! Your hobby requires math :P

  • Like 1
Link to comment
Share on other sites

... So, what's the max number of strings I can have on a light controller? Would you believe it if I said 'Nearly unlimited'? Well, not really unlimited, but a whole lot more than you expect:

In the above example I showed where you could have 24 strings on a single channel. And you can. All day long. But that's not really the MAX, that's the MAX at FULL BRIGHTNESS. Can you run 48 strings without burning up a triac or controller? Sure! just keep the intensity turned down.

Now wait a second! Don't think you can run 48 strings at 50%! What we are talking about is electricity and that means it's not a linear relationship. If I remember my theory correctly, dividing the duty cycle (of the AC wave) in half, does not mean a one-half reduction in amperage consumed.

... which is why when we talk about load per channel we always tend to talk in Maximums. That keeps your equipment safe.

Sorry folks. Remember when your 10'th grade math teacher told you you would someday need what he/she was teaching? Surprise! Your hobby requires math :P

all the time in school I always thought I won't use math everday so whats the big deal,,,,,,,,,then I ended up a machinist :) Edited by james campbell
Link to comment
Share on other sites

Sorry folks. Remember when your 10'th grade math teacher told you you would someday need what he/she was teaching? Surprise! Your hobby requires math :P

Mike, my math teacher said I didn't have to learn math if I have friends later in life that knew math. So thank you for being around. :) You saved me from regretting to have done better in math.

Link to comment
Share on other sites

Shall we listen to somebody with under 100posts or somebody with over 1,000 plus??? There is your basic math.

  • Like 2
Link to comment
Share on other sites

Shall we listen to somebody with under 100posts or somebody with over 1,000 plus??? There is your basic math.

To me it don't matter.

As long as they know math and are a friend. I'm going with my teacher's saying back in the day. Let someone else do the math :P

Edit: well..... maybe that wasn't her exact words but that's what I got out of it. :lol:

Edited by Santas Helper
Link to comment
Share on other sites

"GCM$ d-- s++:++ a? C++++(6$ net$ cob$ cic$ db2$ LN$ php$ ms$) UL+$ P--- N+ W+++++$ O+ M-- t+@ 5-- X+++ R tv+ b++ DI++++ D---- G e+++ h+++ r*"

Sorry I can't resist (and I don't blame you if you want to blast me) but do you also do lights.....

Link to comment
Share on other sites

"GCM$ d-- s++:++ a? C++++(6$ net$ cob$ cic$ db2$ LN$ php$ ms$) UL+$ P--- N+ W+++++$ O+ M-- t+@ 5-- X+++ R tv+ b++ DI++++ D---- G e+++ h+++ r*"

Sorry I can't resist (and I don't blame you if you want to blast me) but do you also do lights.....

There is a translation of that code somewhere around here....

Link to comment
Share on other sites

... So, what's the max number of strings I can have on a light controller? Would you believe it if I said 'Nearly unlimited'? Well, not really unlimited, but a whole lot more than you expect:

In the above example I showed where you could have 24 strings on a single channel. And you can. All day long. But that's not really the MAX, that's the MAX at FULL BRIGHTNESS. Can you run 48 strings without burning up a triac or controller? Sure! just keep the intensity turned down.

Whoa Mike, I think we are getting a-little off here, there are infinite possibilities to try to explain how much lights can be controlled per channel... you're r getting into intensities, and loads etc etc... The question, logically speaking, was how much can a light o rama handle on a mega tree, considering the mega tree has 16 channels and each channel has the same amount of lights, am i not correct?

I'm sure that one point in time trinidad will turn all the lights on his controller on full, and his mega tree will contain the same amount of lights per channel, otherwise it will look odd?

Sorry folks. Remember when your 10'th grade math teacher told you you would someday need what he/she was teaching? Surprise! Your hobby requires math :P

My teacher always told me one thing, a question may have one thousand answers, but think about it using common sense and answer with the most logical answer.

Again if the question was how much is the MOST possible light strings cana light o rama control given the circumstances, then id be in the wrong, but not this time.

Edited by Arteom
Link to comment
Share on other sites

I'm sure that one point in time trinidad will turn all the lights on his controller on full, and his mega tree will contain the same amount of lights per channel, otherwise it will look odd?

Why does he have to turn them all on at once? Say 8ch are white and 4ch are red and 4ch are green (my megatree; red and greens are "up and overs"). Why should he have to turn them all on at once. Nothing odd about solid white, using just half the channels. Or solid green with faint (50%) white every other section. Etc., etc., etc. Or what about having a rule that whenever red is turned on a prop, that green will never be on at the same time on the same prop (and vice versa).

My teacher always told me one thing, a question may have one thousand answers, but think about it using common sense and answer with the most logical answer.

Again if the question was how much is the MOST possible light strings cana light o rama control given the circumstances, then id be in the wrong, but not this time.

Sorry, but I think you are wrong. If you limit yourself to just 5 strings per channel, you are going to require a lot more controllers to control a substantial number of lights. Yes common sense is useful (and rare) but sometimes you have to think way beyond that level to maximize your potential. Mike is entirely right on the above topic and question.

Link to comment
Share on other sites

You could make those assumptions, but that won't make them true.

There is nothing that says the OP doesn't want to make a 4 section tree with 3 colors each using 1 string (12), a VERY FULL full-white tree using 24 strings (1), strobes (1), and a topper (2).

Or perhaps he wants an 8 section 2 color tree that is 75' tall which is going to require 9 strings per section.

Or what about Mini's that only draw .2A/100? (those are called 'Energy Savers')

Or users who run their lights at a max of 80% brightness to save energy and extend bulb life?

Or..... (can you see the myrad of different options here?????)

So, the correct answer is: 8A per channel, 15A per side, not x number of strings per channel.

What you are proposing is a short-cut answer which is incorrect: In the world of electricity, there are no short cuts: do the math or risk killing a channel, a controller, or yourself.

  • Like 3