| Upgrading 1602W to 40amp, question on what wires I need to replace | Rate Topic |
| Author | Post |
|---|
| Posted: Sunday January 29th, 2012 09:14 pm |
|
1st Post |
|
imacericg Member
|
I am upgrading my 1602W to 40amp, and I have upgraded the power supply cords to 12AWG and used new 20 amp plugs. But I also see that the power goes through the switch, then to the fuse before it gets to the board. Do I need to upgrade the short cords that goes through the switch and to the fuse to 12 AWG as well? Thanks, Eric
____________________ Huntersville Christmas Lights Download my free sequences |
||||||||||||||
| |||||||||||||||
| Posted: Monday January 30th, 2012 12:13 am |
|
2nd Post |
|
wbottomley Member
|
You will need to if it's smaller than 12AWG. And... change the fuses to 20 amp as well.
____________________ High Country Lights + Free Sequences |
|||||||||||||
| ||||||||||||||
| Posted: Tuesday January 31st, 2012 01:55 am |
|
3rd Post |
|
imacericg Member
|
Thanks William. I assumed that I had to replace all of the power wires with 12AWG, but couldn't find anything to back that up either way. You working on RGB strips yet?
____________________ Huntersville Christmas Lights Download my free sequences |
||||||||||||||
| |||||||||||||||
| Posted: Monday February 6th, 2012 08:37 pm |
|
4th Post |
|
LightORamaDan One of your administrators
|
At one time, many years ago, we would condone the upgrade of the LOR1602W to 40 amps. One we added the inner plate with We no longer do. If one were to attempt to do so with a LOR1602W with an inner panel, it would not be a simple matter of changing wires. 1. You need to remove the inner panel and there is no real reason to keep it because the switch and fuse holders cannot be used. 2. You would wire your 12awg power cords directly to the circuit board. Connecting to the Input (Hot and Neu) terminals. (NOT THE JUMPER TERMINALS THAT ARE USED WHEN USING THE INNER PANEL). 3. You would place fuses directly on the circuit board. Not that I recommend that this be done but if someone did do it then that would be the way to do so. Dan
|
|||||||||||||
| ||||||||||||||